Re: grounding a sub panel
Roger: I know you are aware that a continuous metal path is OK if not bonded at both panels. 250.32.2.
This was the issue when I got trashed for stating "there is no code section that requires a neutral/ground separation at a panel". The code section is to eliminate parallel neutral paths. The method for doing this is not spelled out.
A three wire cable assembly, in a dwelling, does not create parallel paths.
The neutral is not permitted to be grounded (earthed)on the load side of a service, the connection at a panel for ground fault purposes was not considered grounding (earthing).
Three wire, cable supplied panels, were supplied by SE cable, W/bare neutral/ground conductor until 1996.
The change to 4 wire, with a reduced size safety ground conductor for fault clearing was started in 1996, by a select committee. No one could contest, or debate, the personal decisions, and misunderstandings that created the changes.
This change caused a higher impedance to be present in the fault path, and elevated the neutral/ground voltages. This is not forward engineering, it is two steps back.
Roger: I know you are aware that a continuous metal path is OK if not bonded at both panels. 250.32.2.
This was the issue when I got trashed for stating "there is no code section that requires a neutral/ground separation at a panel". The code section is to eliminate parallel neutral paths. The method for doing this is not spelled out.
A three wire cable assembly, in a dwelling, does not create parallel paths.
The neutral is not permitted to be grounded (earthed)on the load side of a service, the connection at a panel for ground fault purposes was not considered grounding (earthing).
Three wire, cable supplied panels, were supplied by SE cable, W/bare neutral/ground conductor until 1996.
The change to 4 wire, with a reduced size safety ground conductor for fault clearing was started in 1996, by a select committee. No one could contest, or debate, the personal decisions, and misunderstandings that created the changes.
This change caused a higher impedance to be present in the fault path, and elevated the neutral/ground voltages. This is not forward engineering, it is two steps back.