Could anyone please comment on the following grounding situation?
There is 1 Main Service Panel and 1 Overflow Subpanel in the same building, and 1 Subpanel in a detached garage.
The Main Panel has its Neutral bar and Ground bar bonded to each other and to the case.
The Overflow SubPanel is directly under the Main panel in the same building, it has its Neutral bar isolated in plastic mounts, and its Ground bar bonded to the case.
The Detached Garage Subpanel also has its Neutral bar isolated in plastic mounts, and its Ground bar bonded to the case.
The connections between the three panels are with 8/3 wire: Red/Black/White/Bare-Copper.
A 40amp 2-pole breaker in the Main Panel is connecting the 2 hot Red and Black wires to the Hot bar lugs on the Overflow Subpanel. The White wire is connected to both panel's Neutral bars, the Bare Copper wire is connected to both panel's Ground bars.
A 40amp 2-pole breaker in the Overflow Subpanel is connecting the 2 hot Red and Black wires through 30 feet of buried conduit to the Hot bar lugs on the Detached Garage Subpanel. The White wire is connected to both panel's Neutral bars, the Bare Copper wire is connected to both panel's ground bars.
First question: Most importantly, is this configuration electrically safe? What dangers are there?
Second question: Is this code compliant? The garage was built in the 1960s, would it be grandfathered under older code?
Any comments greatly appreciated.
There is 1 Main Service Panel and 1 Overflow Subpanel in the same building, and 1 Subpanel in a detached garage.
The Main Panel has its Neutral bar and Ground bar bonded to each other and to the case.
The Overflow SubPanel is directly under the Main panel in the same building, it has its Neutral bar isolated in plastic mounts, and its Ground bar bonded to the case.
The Detached Garage Subpanel also has its Neutral bar isolated in plastic mounts, and its Ground bar bonded to the case.
The connections between the three panels are with 8/3 wire: Red/Black/White/Bare-Copper.
A 40amp 2-pole breaker in the Main Panel is connecting the 2 hot Red and Black wires to the Hot bar lugs on the Overflow Subpanel. The White wire is connected to both panel's Neutral bars, the Bare Copper wire is connected to both panel's Ground bars.
A 40amp 2-pole breaker in the Overflow Subpanel is connecting the 2 hot Red and Black wires through 30 feet of buried conduit to the Hot bar lugs on the Detached Garage Subpanel. The White wire is connected to both panel's Neutral bars, the Bare Copper wire is connected to both panel's ground bars.
First question: Most importantly, is this configuration electrically safe? What dangers are there?
Second question: Is this code compliant? The garage was built in the 1960s, would it be grandfathered under older code?
Any comments greatly appreciated.