Re: Grounding an RV Power Outlet Pedestal
Thanks for all of the replies on this one. I have to get some final clarification, however. I am clear on the NEC in article 551.76 (A), where it states that exposed non-current carrying metal parts of fixed equipment, metal boxes, cabinets, and fittings that are not electrically connected to grounded equipment shall be grounded by a contious equipment grounding conductor run with the circuit conductors from service equipment or from the transformer of a secondary distribution system.
Now, 551.76 makes no mention of a grounding electrode system (ground rod), but under 250.32 Buildings or Structures Supplied by Feeder Circuits, which an RV Pedestal would be included under, a grounding electrode system is required and must be installed according to 250.50.
So, for final clarification, both a grounding electrode system (ground rod) and a continous grounding conductor connected to service equipment or a secondary transformer is required for each pedestal. Do I have my facts straight?
Thanks in advance.