Is it required to run a GEC to gas pipe for the service, or can gas pipe be bonded by the branch circuit feeding the heater.
250.52(B) Not Permitted for Use as Grounding Electrodes.
The following systems and materials shall not be used as
grounding electrodes:
(1) Metal underground gas piping systems
(2) Aluminum
FPN: See 250.104(B) for bonding requirements of gas
piping
250.104(B) Other Metal Piping. Where installed in or attached to
a building or structure, a metal piping system(s), including
gas piping, that is likely to become energized shall be
bonded to the service equipment enclosure, the grounded
conductor at the service, the grounding electrode conductor
where of sufficient size, or the one or more grounding electrodes
used. The bonding jumper(s) shall be sized in accordance
with 250.122, using the rating of the circuit that is
likely to energize the piping system(s).
The equipment
grounding conductor for the circuit that is likely to energize
the piping shall be permitted to serve as the bonding means.
The points of attachment of the bonding jumper(s) shall be
accessible.