I see maybe I misunderstood IG. So what you are saying. Let’s see example- you have transformer N-G bond that GEC is bonded to main busbar. Are you saying if the IG is bonded to this busbar is correct?IG's are typically run either to the point where the MBJ is located in the service or to the X0 of a transformer. If they ran it all the way back to the service it's probably done correctly if all of the IG rules are followed.
I see maybe I misunderstood IG. So what you are saying. Let’s see example- you have transformer N-G bond that GEC is bonded to main busbar. Are you saying if the IG is bonded to this busbar is correct?
I agree. We would see them in every office building and they were rarely installed correctly. This was the existing IG connection for all of the system IG-EGC's in a post office that we were modernizing. The red conductor went directly to the IG bus in the panel.common in the 80's. but they were rarely done properly. hardly any i ran across were done even close to infinitys diagram
Dismantled many like this.I agree. We would see them in every office building and they were rarely installed correctly. This was the existing IG connection for all of the system IG-EGC's in a post office that we were modernizing. The red conductor went directly to the IG bus in the panel.
View attachment 2566415
Just the opposite is true.Contrary to opinions I have heard here, each IG receptacle must have its own ground conductor home run back to the service panel ground bar. You can't run one home run and tap off of it. That would cause noise and ground currents to circulate among the connected devices.
How about in a situation where you have two SDS systems where 480V is your main and you have another 208V step down transformer.An IG circuit circuit should use the same length Hot, Neutral & EGC wires.
An analog signal IG circuit should be designed so that the pathways from it's IG receptacle to receptacle is as short as practicable. The idea is to keep all the units chassis at about the same potential.
There are no rules that say you cannot tap or splice the IG conductor.How about in a situation where you have two SDS systems where 480V is your main and you have another 208V step down transformer.
Your electronics are fed from 208V so does that mean you need to run the IG circuit back to the 480V GEC?
U can not tap or splice IG so, can you terminate IG circuit from GEC to busbar inside electronics room?
Does that mean you size based on the sub panel size for EGC or can be for example in this case if the electronics is on 30A breaker can bring 10AWG IG EGC ?Every time I have done IG, wich is very few times, the IG was just like a 2nd EGC and was run with and spliced when the circuit conductors spliced.
They land on a floating ground bar in the panel, which has wire back to the transformer like pictured in post 5.
Except most if not all of the IG systems I did were 60/120V.
There is still quite a bit of noise on a EGC to this day, some occupancy sensors still use the ECG as a return conductor for their little internal power supply.
The IG is sized per Table 250.122, just like any other equipment grounding conductor, unless the specs call for a larger size.Does that mean you size based on the sub panel size for EGC or can be for example in this case if the electronics is on 30A breaker can bring 10AWG IG EGC ?
Also so IG is not GEC correct?
Ok. If i understand all this facilities that bond 1/0AWG to independent rod or building steel are doing it wrong.The IG is sized per Table 250.122, just like any other equipment grounding conductor, unless the specs call for a larger size.
it is not a grounding electrode conductor, it is an isolated equipment grounding conductor, but an more correct name would have been insulated equipment grounding conductor as the word isolated results in a lot of confusion.
Yes they are doing it wrong and in violation of the requirements of the NEC.Ok. If i understand all this facilities that bond 1/0AWG to independent rod or building steel are doing it wrong.
The electronic are protected already with EGC run with the feeder when/if fault occurs. To bring IG to telecom busbar and feed #6AWG to few cabinets will help improve noise
When you say IG has to follow same rules to normal EGC, size wire based on 250.122 and must be run with the feeders. How can you accomplish this with IG that has to go back to the transformer Xo, unless this is exception?The isolated equipment grounding conductor is still a fault clearing conductor and must follow all of the rules that apply to the normal equipment grounding conductor, except that they are permitted to be run back to the location of the main or system bonding jumper.
You run both a EGC and an IG.When you say IG has to follow same rules to normal EGC, size wire based on 250.122 and must be run with the feeders. How can you accomplish this with IG that has to go back to the transformer Xo, unless this is exception?