blue spark
Senior Member
- Location
- MN
Hi folks! Got a couple of questions regarding metal buildings. What I have here is a post and beam Morton building. 2- 200amp services general/off-peak. On the metal framed steel buildings we always make the frame part of the grounding system. There is no metal framing on this building. There are no footings. The slab (6") will float on top of 2" of certifoam to insulate the wirsbo in the slab. So this slab is not in contact with earth. ?#1 20' of #4 bare in the dirt under the foam plus #6 solid bare to a rod outside going to satisfy code? Water line is plastic. ?#2 Since there is no metal frame, I'm assuming I have to bond both sides of the "skin" to the panel. I cannot find this in the code. Last year we were told we had to do this on another building. Where is this rule located?