blue spark said:On a side note, I brought the #6 bare GEC in the building from below grade and protected it with EMT up to the panel. I was informed that this creates a choke? He "suggested" I put it in sched 80 pvc instead. Anyone ever heard of this?
Yes, the AHJ is correct. If you use a metallic raceway for the GEC, it must be bonded to the GEC at both ends usually via a bond bushing. RNC is definately the better choice.