inspector23
- Temecula, CA
When connecting the grounding for the light standards in a parking lot, the electrical contractor (EC) simply took a # 4 bare copper wire and properly clamped it with a UL listed clamp to the reinforcing bars of the concrete cylinder prior to pouring the concrete in the cylinder.
When it came time to hook up, the EC took the other end of the bare copper wire and attached it to the factory lug provided inside the handhold of the post. He ran two #10 AWG's from the panel to the light fixture for the 240 V system.
My understanding was he needed to have an additional wire (properly sized) to bond the pole back to the power source. His contention is he does not, citing article 410.21 (2002 code)and the definition of equipment grounding conductor.
Ideas?
[ September 23, 2005, 04:05 PM: Message edited by: inspector23 ]
Ideas?