Hi,
What (in ohms) is the minimum reading to earth at the service ground.
What (in ohms) is the minimum reading to earth at the service ground.
How? The earth is too poor of a conductor to make any real reduction in touch voltage. If you apply 120 volts to a ground rod and measure the voltage between the rod and the earth a foot away, you will find about 80 volts. A very large portion of the voltage drop occurs very close to the rod.... but basic Ohm's Law does show reducing ground resitance does help to reduce touch voltage which is lethal at above 30-volts.
That is a true statement, but it is also the reason why a driven rod has no real effect on the touch voltage.My statment is that OHM'S LAW doesnt lie.
In the high voltage switch yard, there will be a grid of copper conductors not far below the surface. This is connected to the grounding electrode system for the yard. I though that the intent of this was to reduce the step and touch potential within the yard in the event of a fault. I have read that under fault conditions, the voltage of the yard grounding system can be 5000+ volts above that of the earth a 100' or so away from the yard. If the intent is to create a reduction in the step and touch voltage, why would you want to use a high resistance ground cover?Asphalt has a high resistance. Crushed rock also. Notice how high voltage switching stations all have crushed rock.
This is one of the most common fallacies about grounding. The earth is just too poor of a conductor to drive the voltage of the electrical system down to ZERO volts to earth. The relative impedance of the grounding electrode system is many 100s of times greater than that of the main fault return path. Changing the grounding electrode impedance from 25 to 5 or even 1 ohm really doesn't make much difference on the voltage that appears on the electrical grounding system under fault conditions. The voltage that will appear on the grounding system under fault conditions will equal that of the voltage drop of the fault return path. Look at a 200 amp service with a 150', 2/0 copper service and a fault in the panel on the load side of the breaker. Based on the time/trip curve, a 4000 amp fault could take as long as one second to clear. The voltage drop on the 150', 2/0 grounded conductor would be 58.02 volts. This 58 volts will appear on everything that is connected to the electrical grounding system until the fault is cleared. A 25 ohm grounding electrode would drop this voltage to 57.98. A 1 ohm grounding electrode system would drop this voltage to 57.19 volts. This voltage will be between any part of the electrical grounding system and the earth at any point more than a few feet from the grounding electrode. The earth connection does not give any increase in electrical safety when ground faults occur within the building electrical system. The most important part of an electrical safety under ground fault conditions is to provide a very low impedance ground fault path back to the power source. This is only accomplished by bonding all nonconductive parts of the electrical system back to the grounded conductor at the service.When a conductor or metal equipment is connected to an Earth electrode, it is forced to take the same ZERO potential as the Earth. Any attmept to raise the voltage of a grounded object results in current passing over the connection until the potential of the object and the Earth are equal.