Re: Grounding and bonding
Ed,
I don't agree. I think that in both cases, the victim receives a 60 volt shock. While I agree that there will be a total of 60 volts dropped across the series/parallel circuit created by the 3 grounding electrodes, there will also be 60 volts dropped across the victim. The drawing makes it appear that the human and R7 are in parallel with each other and then in series with paralleled R1 and R2. I don't think that is correct. What we really have is the 37.5 ohm series/parallel resistance of the R1, R2, and R7, in parallel with the human. This is a parallel circuit and the voltage across each of the legs must be the same, so he will still receive a 60 volt shock.
The only way to reduce the voltage across the victim is to reduce the impedance of the fault return path enough to reduce the voltage drop on this path. If you place a second EGC in parallel with R3, you would have a 1600 amp fault, a drop of 56 volts in the transformer, 24 volts in the feeder and 40 volts for the two parallel EGCs.
Don