joeyww12000
Senior Member
- Location
- Chatsworth GA
I terminated a 120/208 transformer yesterday. The xo/ground bond was made at the transformer. Heres how I did my grounding and bonding. From XO, GEC to building steel, bonding jumper to case frame. From case frame, Incoming EGC from 277/480v panel with primary conductors for transformer feed, EGC with secondary conductors feeding 120/208v panel. OK, specs called for 1/0 cu for GEC, #6 cu for EGC's on Primary and Secondary sides of transformer. I also used a #6 cu for my bonding jumper from xo to case frame, was that correct? My question stems from 250.102 (c) and (d). Is the primary side of a transformer considered "supply side of service" and secondary side considered "Load side of service"?