Re: grounding and grounded conductors on same lug
I think 408.21 just makes it clear that tyou dont put anything but the grounded conductor in the terminal. In other words just the one wire. The last paragraph points you to where you need to be and that is in article 250. If in fact this is a service panel and not a subpanel then it is not only permitted for these conductors to be tied together it is required. You still need to use only one wire on each terminal but for instance say on a service main without a terminal bar you can use indivdual lugs and stack them on a single stud.If there is a terminal bar and it is Identifeid for the use then 408.20 again permits it. Couldnt tell for sure from you post whether you are talking about a main service panel or a sub.rcarrol is dead on in pointing out that you may only have one wire on each lug. A double barrle lug could be used also to tie each of these together where it is required also.