A contractor recently installed a MCC in our plant. The equipment consists of VFD,s, motor starters, and a PLC. This panel is fed with 480v. three phase power. In order to obtain 120v. control power, a 15Kva transformer 480v. to 120v. single phase was installed outside of the panel. While troubleshooting a control problem, I discovered that the neutral was not bonded to the grounding conductor for the control circuit. According to NEC Art. 250.20 B,D I feel that this is a code violation. The contractor tells me the neutral does not have to be bonded but cannot cite any code reference. Who is right?