Grounding/Bonding a Control Transformer

Status
Not open for further replies.

kuhala

Member
A contractor recently installed a MCC in our plant. The equipment consists of VFD,s, motor starters, and a PLC. This panel is fed with 480v. three phase power. In order to obtain 120v. control power, a 15Kva transformer 480v. to 120v. single phase was installed outside of the panel. While troubleshooting a control problem, I discovered that the neutral was not bonded to the grounding conductor for the control circuit. According to NEC Art. 250.20 B,D I feel that this is a code violation. The contractor tells me the neutral does not have to be bonded but cannot cite any code reference. Who is right?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Grounding/Bonding a Control Transformer

Look at 250.21(3). If all of the conditions in (a) though (d) are met the control transformer is permitted to be an ungroundec system.
Don
 

kuhala

Member
Re: Grounding/Bonding a Control Transformer

Absolutely! I did not mention the fact that these conditions,specifically C and D were not met. Thanks
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Grounding/Bonding a Control Transformer

kuhala, if all the conditions of 250.21(3) a thru d are not met then you must apply 250.30 for seperately derived systems.

Dereck
 