I have a 120/240 volt, 200 amp main, single phase, feed through load center outside a single family dwelling unit as the main disconnect. Several 120 and 240 volt loads are derived from this load center. The grounding electrode system consists of #4 solid bare copper to three ground rods and the cold water system. The neutral bar is bonded to the enclosure at this location. A #4/0 AL SE cable is connected to the feed through lugs on the bus bars feeding another 120/240 volt, 200 amp, main lugs only, single phase load center inside the dwelling unit. Several 120 and 240 volt loads are derived from the inside load center. The neutral bar is bonded to the enclosure at this location also, but is not bonded to the cold water system or the grounding electrode system. I have not found this exact situation in article 250 of the handbook and am looking for the correct way to ground and bond the inside load center. Closest situation I found was article 250.32, Two or More Building or Structures Supplied from a Common Service. Can I just run another #4 solid bare copper grounding electrode conductor to the existing grounding electrodes?