nakulak said:"drain . . .circuit" is a term that in my opinion merely obfuscates and confuses.
The High voltage and Data/communication/signal electricians use this ?drain circuit? terminology and mindset not me, this is the confusion I?m trying to point out.
nakulak said:I think your information is well intentioned, and is a good start for a 1-page presentation (if that's what it is).
No that is not what I intend to convey. I?m not even trying to teach but I am making an observation that over the years has proven to confuse electricians with different backgrounds. My intent is to point out that different types of electricians use and understand grounding and bonding differently causing confusion between others and us.
This is what I meant to say in [or by] my original post:
Even the label ?electrician? is too broad and not descriptive enough causing confusion regarding installations especially grounding and bonding. These different electrical trades DO ground commonly to control lightning and transformer failures but that?s it, they do NOT share common reasons for ground fault control (equipment ground conductors & effective ground fault path) or even unbalance load return path, the grounded conductor (neutral)?
In summary we really have 3 worlds colliding with electricians and their use of grounding:
1 High voltage = return path for the unbalanced load/drain to open circuit/effective ground fault path/lightning & transformer failure control
2 Data/communication/signal = drain to clean circuit/lightning & transformer failure control
3 Premises wiring of 600 volts and less = lightning & transformer failure control ONLY!
My hope is to untangle the broad use for reasons to ground while untangling the broad use of the label ?electrician?