OK, I thought I knew this stuff, but for some reason this is giving me a headache.
I just installed a meter/main outside which feeds a panel inside (approx 6 feet away). The service is overhead and is feed by THHN via RMC to the meter/main. From the meter main to the panel is #2 Romex.
Isn't the panel a sub panel and therefor CANNOT have a neutral/ground bond?
I ran the #6 GEC from the rods to the water pipe to the meter/main. The EGC that is bunled in the Romex is connected to the bonded ground bus in the meter/main and is attached to the ground bus in the panel which is not bonded.
Normally I use a meter can and a main/Load center so bonding at the meter is unusal for me.
Thanks.
I just installed a meter/main outside which feeds a panel inside (approx 6 feet away). The service is overhead and is feed by THHN via RMC to the meter/main. From the meter main to the panel is #2 Romex.
Isn't the panel a sub panel and therefor CANNOT have a neutral/ground bond?
I ran the #6 GEC from the rods to the water pipe to the meter/main. The EGC that is bunled in the Romex is connected to the bonded ground bus in the meter/main and is attached to the ground bus in the panel which is not bonded.
Normally I use a meter can and a main/Load center so bonding at the meter is unusal for me.
Thanks.