tryinghard
Senior Member
- Location
- California
I agree, maybe the terminology can be:iwire said:The question in my mind is why do we call it an effective ground fault path?
The 'ground' has nothing to do with opening the source over current device..
It should be called 'an effective fault path' or maybe 'effective bond fault path to source.
I agree with Don, almost all the times the NEC says 'ground' they are actually talking about bonding.
Very few conductors under the NEC have anything to do with the 'dirt'.
Return Conductor (grounded conductor/neutral)
Bonding (equipment grounding conductor)
Frame Bonding (separately derived systems)
and Earthing (electrode & it?s conductor)
We?ll have to rename GFI & GFCI?s ? BFI & BFCI?s or circuit trip unit?
I don?t have my ?05? book at home but I do have my ?02?, have you ever noticed 250-26?
Mike Holt has a good definition of a true neutral conductor in: Understanding the National Electrical Code, 2nd edition, based on ?96?, ?For a ?grounded conductor? to be a true ?neutral?, there must be an equal potential between the grounded conductor and all phases of the system?, This is like 1PH 3W of 3PH 4W wye not delta.
The neutral conductor really is grounded at the source but it does not require the ground to function safely with a fault, unless the serving grounded conductor is broken wow how remote could that be? Broken grounded conductor happens then a fault happens?
I think because the neutral conductor commons with ground at the source it will always be referred to as the grounded conductor especially with future old timers (like those who transition through this inevitable change) and utility linemen. Sure would be nice to clean up the terminology though.