jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
I would say that your tactic of editing my comments so that they make your point is poor etiquette. If you were to include the whole comment you would read that I have not contradicted myself.
I was just trying to keep the thread from being too cluttered and I did not remove anything that would change my opinion about your comment. I did forget to mention that I do not think that lightning is what the insurance inspector in the OP had in mind.
Bonding reduces arcing vs not bonding for a ground fault by reducing the duration the arc is allowed to persist. An object that is not bonded could arc indefinitely until starting a fire.
Why would an object that is supposed to be bonded but is not bonded arc indefinitely and start a fire? I cannot think of a situation in residential AC wiring where this would be meaningfully true. Moreover, there are types of arcing (e.g. series arcing), that bonding can play no part in stopping.
An object that is bonded will arc for a very short time because the OCPD will trip on a ground fault.
And an object that is not bonded won't arc at all if not in contact with other bonded objects. It could be energized and thus a potential shock harzard or arc hazard to other objects, and that is certainly dangerous, but that situation is not accurately described by the phrase 'bonding prevents arcing.'
This point you are trying to make is only relevant to ground faults.
I think the point I'm making is relevant to the entirety of low voltage wiring, and perhaps the entirety of wiring under the scope of the NEC. Perhaps I'm wrong, but no evidence has been presented in this thread to convince me otherwise.
There are other reasons why bonding and grounding help reduce arcing. Do you dispute these as well?
Not entirely, but I have not seen any examples given that seem relevant to the 240V residential wiring involved in the OP, or even any that fit within the scope of wiring covered by the NEC. Again, it seems to me that the primary intent of bonding in the NEC is to cause arcing when there is a fault, with the intent of tripping protective devices.
The OP made a reference which I believe was intended to convey that the home inspector had no idea what he was talking about. I believe the OP is substantively correct on that point.