I'm pretty sure I know the answer to this one, but I have to ask...
We are doing work in a residential MDP which is in a closet inside the dwelling. There is an external service disco with OCPD. The neutral is bonded to ground at the disco.
Inside the MDP the neutral and ground bars are bonded (obviously a problem), the branch circuit neutrals and EGCs are all connected willy-nilly to whichever bar the electrician(s) fancied at the time, and the inside of the enclosure is a rat's nest.
My question is this: Is there any wiggle room in the NEC that would allow our guys to fix the problem by unbonding neutral from ground at the disco instead of untangling the rat's nest, unbonding the bars, and separating the branch circuit ECG's from the neutrals?