Re: Grounding ( Bonding) recptacles for PCs
All of what you reference relates to multiple computers on a network or interconnected. The last document you provided was last revised in 1997, don't know when it was originally written.
There were many networks wired with "thinnet" or RG-58 at the time with it's copper shield running from computer to computer. Many also were linked with RS232 cables. It was important to minimize stray currents in such cables as they could indeed disrupt data transmission, and those were the days when IG receptacles were born.
Today with 10/100 baseT ethernet and fiber, maintaining a single point ground for all machines is not necessary, IG receptacles are not necessary. A stand alone machine certainly does not require anything other than the ground necessary for safe operation.
I think your information is a bit dated and not relevant to todays equipment.
-Hal
All of what you reference relates to multiple computers on a network or interconnected. The last document you provided was last revised in 1997, don't know when it was originally written.
There were many networks wired with "thinnet" or RG-58 at the time with it's copper shield running from computer to computer. Many also were linked with RS232 cables. It was important to minimize stray currents in such cables as they could indeed disrupt data transmission, and those were the days when IG receptacles were born.
Today with 10/100 baseT ethernet and fiber, maintaining a single point ground for all machines is not necessary, IG receptacles are not necessary. A stand alone machine certainly does not require anything other than the ground necessary for safe operation.
I think your information is a bit dated and not relevant to todays equipment.