rhamblin
Senior Member
- Location
- Kaukauna, Wisconsin
I've got a few questions regarding what is necessary per the NEC regarding bonding. My recent project was to run power to a new piece of equipment, When I got the conduit to the disconnect I noticed that I would be entering a eccentric knockout. I used a grounding bushing, because I would not be removing to the largest hole. Was this overkill?
When I pulled out the codebook, the only article that mentions eccentric and concentric supplemental bonding is at Services. Does that mean that it isn't necessary feeding into a disconnect? The run feeds off of a 480V Bus, there are no transformers involved. So it isn't a service.
Following on, are we required to use a bonding bushing every time we run a 1/2" conduit through 1/2" eccentriced hole with a 3/4" k.o.? That can't be right...
Next question, if in my situation the eccentric k.o. is not considered a legitimate bonding connection and I don't use a grounding bushing or anything, but do pull a grounding conductor in and terminate it at both ends, would this suffice? Essentially even thought enclosure isn't bonded via the conduit, because of the eccentric ko, does the grounding conductor make up for it?
When I pulled out the codebook, the only article that mentions eccentric and concentric supplemental bonding is at Services. Does that mean that it isn't necessary feeding into a disconnect? The run feeds off of a 480V Bus, there are no transformers involved. So it isn't a service.
Following on, are we required to use a bonding bushing every time we run a 1/2" conduit through 1/2" eccentriced hole with a 3/4" k.o.? That can't be right...
Next question, if in my situation the eccentric k.o. is not considered a legitimate bonding connection and I don't use a grounding bushing or anything, but do pull a grounding conductor in and terminate it at both ends, would this suffice? Essentially even thought enclosure isn't bonded via the conduit, because of the eccentric ko, does the grounding conductor make up for it?