I looked at the above-mentioned code sections, and am left with a related question. Situation is a residential service with a main disconnect that has a threaded hub bolted to the top of it, and a close nipple that is lock-nutted to the bottom of the meter base through the largest KO, so there are no concentric rings left. The neutral conductor is bonded in both enclosures, so the nipple is merely the service raceway.
So, must a bonding locknut or bushing be installed on the top of the nipple? We're not allowed to land any GECs in meter bases since we're sealed out of them and they can't be inspected. It seems we likewise wouldn't have access to a nipple bonding device's connection. If we none-the-less must bond the nipple, where do we land the other end of the conductor, in the meter or through the nipple into the disconnect?
So, must a bonding locknut or bushing be installed on the top of the nipple? We're not allowed to land any GECs in meter bases since we're sealed out of them and they can't be inspected. It seems we likewise wouldn't have access to a nipple bonding device's connection. If we none-the-less must bond the nipple, where do we land the other end of the conductor, in the meter or through the nipple into the disconnect?