john2mcc

Member
if you install 120v multiconductor cable in conduit stubbed up to cable tray feeding space heater ckt's in swgr and there is no ground in the cable will grounding bushings be required?
 

john2mcc

Member
grounding bushings

how do you size the ground on your grounding bushings to the cable tray on parrallel feeds from switchgear to mcc?
 

hurk27

Senior Member
if you install 120v multiconductor cable in conduit stubbed up to cable tray feeding space heater ckt's in swgr and there is no ground in the cable will grounding bushings be required?

250.96(A) allows the raceway and the fittings to be the bonding means.

I would say IMO no your don't need bonding bushings. but there are inspectors who might see different.:roll:
 