Aretae
- at home with both wives
I am an electrician being asked to install a ground that appeared on the latest reved single line. The transformer is a 480V wye step-up to 12kv delta. The ground wire is to be insulated and not be bonded to the equipment ground. Since the transformer resides in a common switchgear enclosure and is not insulated from it, I am concerned that a fault to the steel switchgear enclosue would not be a direct ground fault.
The ground rod for the center tap will reside a couple of feet away from the ground rod for the equipment ground. It appears to me that a fault to the metal enclosure would go out on the equipment ground and then through the earth to the center tap. I think there will be a voltage potential. Am I wrong to think that safety is at risk here? I would rather be wrong and be embarrassed then right and not say anything.
I can upload the relevant portion of the single line if necessary, I am not sure you can see the one I posted at:
http://files.engineering.com/getfil...-b466-d5a7c63700ac&file=a_12kv_iso_Ground.pdf
Thank you,
aretae
Thank you,
aretae