Yes, that is the way I read 250.180 as well.--- Article 250 Part X does not supplement or modify any of the requirements of the previous Parts of Article 250.
I don't see this as true. Here is an example:Unless it is established that the premises 12kV system has a neutral, Article 250 Part X does not ---
Given the limited information we have, one might consider applying 250.182, and grounding the system. Although I don't really know, it is difficult to see the installation specifics from my side of the monitor.
As we all know:
The NEC does not give a receipe for premisis wiring over 1kv like they do for house wiring. There are no cookie cutter systems over 1kv
Grounded, un-grounded, ground detectors, relaying - all design/engineering decisions.
The code panels writing the over 1kv sections appear to know this.
cf