J jgonzalezusnvet Member Nov 25, 2015 #1 Is there a code that requires a copper clamp for the ground rod and or the water main? If not what is the best material to use? JGonzalez
Is there a code that requires a copper clamp for the ground rod and or the water main? If not what is the best material to use? JGonzalez
Pharon Senior Member Location MA Nov 25, 2015 #2 It does not need to be copper, but it does need to be listed for that use type. I've seen them in copper, stainless steel, zinc, and bronze.
It does not need to be copper, but it does need to be listed for that use type. I've seen them in copper, stainless steel, zinc, and bronze.