david
Senior Member
- Location
- Pennsylvania
as Wayne said but,For Equipment Grounding Conductor EGC. The EGC should run inside the pipe between the electric meter and the panel.
As you do an internet search there are manufactures that now providing meter enclosures with a manufactures removable limk that bonds the neutral to the service meter enclosure. In the same way its common for CT cabinets to be manufactured that way.
In some areas it's popular to do as you suggested.
However the bond between the service enclosure neutral bonding back to the meter enclosure is a main bonding jumper not an equipment grounding conductor.
Added: Of course you wouldn't do both, use the manufactures bond and the wire main bonding jumper. That would defeat the intended purpose of using that method.
Also keep in mind main bonding jumpers of the wire type have to be the correct size based on the size and material of your service conductors
Last edited: