I am a municipal inspector and recently had a disagreement with a electrician. I am insisting that he install a grounding conductor within the flexible metal conduit which he installed for lighting whips for ceiling fixtures. He ran EMT to a 1900 box, put in a 6' whip to a control / transformer box for LED wafer light, then added another 6' whip to a second box, and so on. My understanding ( I am not an electrician) is that according to 250.116 (5)(c) of the 2011 NEC, the combined length of the 6' sections of flexible conduit exceeds the maximum of 6' and therefore requires a ground wire.
He insists that because each whip is 6' between boxes that it is not required. The Manufacturer's installation instructions do also specify to connect hot, neutral, and ground wires at each fixture.
I am not trying to be a hard guy, I am only trying to be safe, compliant, and fair. That is why I would love opinions from the members here.
Thank you in advance, the expertise on this forum has been invaluable to me in my occupation.
He insists that because each whip is 6' between boxes that it is not required. The Manufacturer's installation instructions do also specify to connect hot, neutral, and ground wires at each fixture.
I am not trying to be a hard guy, I am only trying to be safe, compliant, and fair. That is why I would love opinions from the members here.
Thank you in advance, the expertise on this forum has been invaluable to me in my occupation.