Say there are 4 A/C units on a building. 2 will have #8 3 phase 208 units and 2 will have #10 3 phase 208 units. There is also a 120 volt GFI outlet for maintenence. Both are going in 1" conduits. One conduit will have 3-#8's, 3- #10's and a #10 green. The other conduit will have 3-#8's, 3-#10's and 2-#12's. The conduits both terminate in the same enclosure.
Can you pull a single green ground wire for both conduits and ground the enclosure or does it take a ground wire for each conduit? Conduits are PVC sch 40 with GRC 90's. Set aside the derating factor because the wire is oversized per unit anyways. Again, one ground wire for both pipes or two, one for each pipe?
Can you pull a single green ground wire for both conduits and ground the enclosure or does it take a ground wire for each conduit? Conduits are PVC sch 40 with GRC 90's. Set aside the derating factor because the wire is oversized per unit anyways. Again, one ground wire for both pipes or two, one for each pipe?