dklecka
New User
- San Antonio, Texas
- Electrical Contractor
In our area there is some disagreement about how to adjust the grounding conductor for voltage drop (VD). 250.122(B) calls for it to be increased the same percentage as the ungrounded conductors. In many sizes that makes sense, but it is extreme especially when considering #12 & #10 conductors. Many Engineers revert to Table 250.122 which makes sense but is a technical violation of the NEC.
The equipment ground seldom becomes a part of the ground fault path except at the equipment, maybe that is why it is called the equipment grounding conductor. Think backhoes & Sawzall’s. When a fault occurs at the equipment the ground path should be the same regardless of the source voltage since when there is a fault the current flow approaches the AIC and the source voltage in response approaches zero.
An example might help to illustrate this disconnect:
A 15FLA 120V/1ph circuit on a 20A breaker 215’ from the panel would require #6 phase/neutral conductors for 3% VD and the ground conductor would also need to be #6 per 250.122(B). Conversely a 46FLA 480V/3ph circuit on a 60/3 circuit breaker 215’ from the panel would require #6 phase conductors and a #10 ground per table 250.122 and 3% VD considerations would not be applicable. In the event of a ground fault at the equipment the AIC would be expected to be greater on the 480V circuit but the ground path is smaller.
Recommend the following change to 250.122(B) (but better language would be appreciated): …however, the grounding conductor size does not need to exceed the size imputed from Table 250.122.