I posted this comment in the low voltage thread and realized that this thread is probably a better for my question. Sorry for the duplicate question.
Here is my question:
I've been doing my research and I understand that power limited circuits with class 2 wiring (i.e. speaker wire from sound amplifiers) is not required to be in raceways when exposed on walls and in ceilings (NEC Art. 725). But, what if class 2 cabling was put in a metallic conduit (such as Flexible Metal Conduit or EMT) to protect the cables? I figure the conduit needs to be grounded and metallic parts bonded because the class 2 circuit output wiring on the amplifier can reach over 50 volts (70volt distributed sound systems). Is it ok to bond the conduit and metal switch boxes to a steel beam framing member and the amplifier will be grounded by the branch circuit receptacle ground conductor? They will both be connected to the electrode grounding system right? Is this method accepted or is there a risk of a potential difference to ground or other hazards. If this is unacceptable, how would I accomplish this ensuring a safe grounded installation?
This is a question I have been pondering for a while and I keep going in circles around NEC codes. Most of the codes are tailored to contractors working with new construction installations. The type of system I mentioned and other sound systems I am concerned with are added well after the initial inspections and construction of the building.
If you have any insight, it would be vastly appreciated.