for an external steel sunshadeAre you concerned with grounding systems for electrical transmission and distribution, or for buildings and structures?
Aircraft maintenance? If so, it’s probably engineered to have lightning and static protection. As far as I remember, the counterpoise can be loop, radial, or combination of both. For sunshade, I would typically see loop configuration set around the sunshade perimeter with at least two wells for periodic inspection/testing.for an external steel sunshade
Yup, did u have a recommendation; in another way did closing the loop have better performance in decreasing resistance or making any form of continuityThat's what we call a "design issue."
No, it is just a normal material storage;; no lightning and static protection is needed ; just a grounding grid to decrease resistance,, my question here is did closing the loop have better performance in decreasing resistance or making any form of continuityAircraft maintenance? If so, it’s probably engineered to have lightning and static protection. As far as I remember, the counterpoise can be loop, radial, or combination of both. For sunshade, I would typically see loop configuration set around the sunshade perimeter with at least two wells for periodic inspection/testing.
I would not worry about the resistance. A grounding electrode system does not need any particular resistance level to do its job, and a lower value does not provide any benefit. I would install the minimum required amount of materials to meet the requirement.No, it is just a normal material storage;; no lightning and static protection is needed ; just a grounding grid to decrease resistance,, my question here is did closing the loop have better performance in decreasing resistance or making any form of continuity
If you are really worried about the resistance, your rods should be at least as far apart as they are deep. Very few triad arrangements, i have seen, meet this requirement.No, it is just a normal material storage;; no lightning and static protection is needed ; just a grounding grid to decrease resistance,, my question here is did closing the loop have better performance in decreasing resistance or making any form of continuity
I’m not too sure if closing the loop did any improvement. I mainly did installs and interconnect everything with cadwelds. Most of my systems were over engineered and required 5-10 ohms of resistance. We had fall of potential testers to make sure everything was meeting requirements but ultimately the contract stated that a third party had to test and certify the system.No, it is just a normal material storage;; no lightning and static protection is needed ; just a grounding grid to decrease resistance,, my question here is did closing the loop have better performance in decreasing resistance or making any form of continuity