Grounding dry type 120/208–277/480v transformers

Status
Not open for further replies.

Jwyattcesg

New member
Location
Plano TX Collin
Have an inspector that says you must use grounding type bushing on conduits entering transformer.
is this a new code requirement I’m not aware of because I have always used plastic bushings
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Unless there are concentric or eccentric KO's and it's over 250 volts to ground they are not required. The GEC in a metal raceway is a different story.
 