Out of habit, I have always used #6 Cu for all GECs. Even for all those100 amp subpanels. According to 250.66, I could have been using #8, correct ?
Thanks, not the biggest mistake I've made, its just a little cheaper and easier to run than #6. But I see the code you are talking about.Yes #8 is permitted typically for 100 amp services. One caveat is that it cannot be run exposed, it needs to be either in raceway or cable armor.
Yes. Must be protected by one of the means listed in (B)(3).Thanks, not the biggest mistake I've made, its just a little cheaper and easier to run than #6. But I see the code you are talking about.
250.64 B (3) Does this mean it has to be in conduit even inside a drywalled wall ?
Running #6 is easier and in the long run cheaper than running #8 cable armor. For #8 GEC's to a water pipe you can use #6 aluminum instead of copper without protection.Thanks, not the biggest mistake I've made, its just a little cheaper and easier to run than #6. But I see the code you are talking about.
250.64 B (3) Does this mean it has to be in conduit even inside a drywalled wall ?
Thanks. #6 AL would probably not work unprotected underground to a rod ?Running #6 is easier and in the long run cheaper than running #8 cable armor. For #8 GEC's to a water pipe you can use #6 aluminum instead of copper without protection.