grounding E C sizing

Status
Not open for further replies.
Yes #8 is permitted typically for 100 amp services. One caveat is that it cannot be run exposed, it needs to be either in raceway or cable armor.
 
Yes #8 is permitted typically for 100 amp services. One caveat is that it cannot be run exposed, it needs to be either in raceway or cable armor.
Thanks, not the biggest mistake I've made, its just a little cheaper and easier to run than #6. But I see the code you are talking about.
250.64 B (3) Does this mean it has to be in conduit even inside a drywalled wall ?
 
Thanks, not the biggest mistake I've made, its just a little cheaper and easier to run than #6. But I see the code you are talking about.
250.64 B (3) Does this mean it has to be in conduit even inside a drywalled wall ?
Yes. Must be protected by one of the means listed in (B)(3).
 
Since an 8 awg GEC needs protection they make 8/1 solid armored cable for people who want that.


However you need different electrode fittings that clamp the armor to bond it and by the time you're done with all that I think it's cheaper to run 6awg

Also on a 200A service you generally need 4awg because of the service conductor size.
 
Thanks, not the biggest mistake I've made, its just a little cheaper and easier to run than #6. But I see the code you are talking about.
250.64 B (3) Does this mean it has to be in conduit even inside a drywalled wall ?
Running #6 is easier and in the long run cheaper than running #8 cable armor. For #8 GEC's to a water pipe you can use #6 aluminum instead of copper without protection.
 