Depends on what your year you're looking at, 2017 is 250.122250.104(A)(1) refers to Table 250.102(C)(1), not Table 250.122.
Cheers, Wayne
Depends on what your year you're looking at, 2017 is 250.122250.104(A)(1) refers to Table 250.102(C)(1), not Table 250.122.
Cheers, Wayne
2017 and 2023 both refer to Table 250.102(C)(1) in 250.104(A)(1), although 2023 adds a 3/0 Cu maximum size.Depends on what your year you're looking at, 2017 is 250.122
If there also is no CEE or structural metal that qualifies as an electrode then yes.So on 200A service if there is plastic water pipe 2 ground rods with #6 conductor is sufficient?
So are the jumpers sizes on 250.66, and a250.53(c) Looks like the gec to from service to underground metal water pipe water should be sized #4 ? since the service has 3/0 ungrounded conductors.