When installing a transformer can you pull in the grounding electrode conductor in the same raceway as the feeder conductors for the transformer?
-The equipment grounding conductors sized accordingly for the transformer feed.
-The grounding electrode conductor coming off MDP main buss that is the location of grounding electrode and location of the main bonding jumper.
-If its done properly with bonding bushing on each end of the emt raceway and bonding in any pull cans ect.
I would like some feed back. I haven’t seen this done, so i could be missing a reason why you cant.
-The equipment grounding conductors sized accordingly for the transformer feed.
-The grounding electrode conductor coming off MDP main buss that is the location of grounding electrode and location of the main bonding jumper.
-If its done properly with bonding bushing on each end of the emt raceway and bonding in any pull cans ect.
I would like some feed back. I haven’t seen this done, so i could be missing a reason why you cant.