I am installing a new 320 amp single phase service (underground) to a building. The service entrance conductors go into a meterbase and then split into two 200 amp disconnects. I have a ufer ground and also a single ground rod (ground rod was required by the POCO). I had run a #4 from the neutral/ground bond point in the meterbase to the ufer sized per 250.66(B). The inspector failed the inspection because he said I needed a grounding electrode conductor sized per table 250.66 (he wanted me to have a 1/0 GEC). I didn't think the sizing in 250.66(B) had anything to do with the size of the service, just run a #4 regardless of the size of service?
Thanks,
Garth
First off 250.66(B) is clear as you surmised that a concrete encased electrode does not need to be larger than a #4
250.66(B) Connections to Concrete-Encased Electrodes. Where
the grounding electrode conductor is connected to a single
or multiple concrete-encased electrode(s) as permitted in
250.52(A)(3), that portion of the conductor that is the sole
connection to the grounding electrode(s) shall not be required
to be larger than 4 AWG copper wire.
Secondly, Table 250.66 is based on the size of your service conductors as in Note 1. Usually with 2 - 200 amp disconnects you would only need a #2 conductor as the grounding electrode conductor but that would be to other electrodes such as water pipe. You would need to use #2 if you had to bond the water pipes.
Note 1 states that you take the cir mil of the service conductors and size the grounding electrode conductor based on the sum of those conductors. Look at 3/0 copper--167800 x 2 = 335,600 . This is equivalent to 350 KCM. The table states #2 for 350 kcm.
If you had a meter main-- no service conductors then you would use Note 2 and then you would be required to use a 1/0 gec