I am installing a new 320 amp single phase service (underground) to a building. The service entrance conductors go into a meterbase and then split into two 200 amp disconnects. I have a ufer ground and also a single ground rod (ground rod was required by the POCO). I had run a #4 from the neutral/ground bond point in the meterbase to the ufer sized per 250.66(B). The inspector failed the inspection because he said I needed a grounding electrode conductor sized per table 250.66 (he wanted me to have a 1/0 GEC). I didn't think the sizing in 250.66(B) had anything to do with the size of the service, just run a #4 regardless of the size of service?