hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
Re: Grounding electrode conductor sizing
#1 Ground rod are not for fault current unless it is at a voltage much higher than what is delivered to our houses!
And what determins the amount of current a ground rod will return to source will be the ground (Earth) not the GEC by no means.
It is the resistance of the rod to Earth connection that comes into play. If you had a rod that was at the minium of 25 ohm's you could attacth a hot 120 volt wire to it and it will only draw 4.8 amp's of current. this would not trip a 5 amp breaker. now raise the voltage to 7200 volts and you now have 288 amps flowing through this wire but because POCO's would never have there primarys fused as high that would heat up a #6 the wire would still be protected. and as far a lightning goes.... Well it goes where it wan't to
Derwith I don't think you have the understanding of it yet!The capability of a ground rod to dissapate the fault current into the earth is limited to what a #6 wire can deliver.
#1 Ground rod are not for fault current unless it is at a voltage much higher than what is delivered to our houses!
And what determins the amount of current a ground rod will return to source will be the ground (Earth) not the GEC by no means.
It is the resistance of the rod to Earth connection that comes into play. If you had a rod that was at the minium of 25 ohm's you could attacth a hot 120 volt wire to it and it will only draw 4.8 amp's of current. this would not trip a 5 amp breaker. now raise the voltage to 7200 volts and you now have 288 amps flowing through this wire but because POCO's would never have there primarys fused as high that would heat up a #6 the wire would still be protected. and as far a lightning goes.... Well it goes where it wan't to