Grounding Electrode Conductor Table 250.66

Status
Not open for further replies.
Stickboy, you're reading the wrong definition, we are not talking about Accessible, we are talking about Accessible (as applied to wiring methods)


Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.

Where do you see a lock in that definition?

Unless the meter enclosure is behind the building finish the wiring in it is accessible

Why do you think it's a code violation to make the connection in the meter can in the first place? I know you say your POCO doesn't allow it but that has nothing to do with the NEC.

It is a common practice and the meter enclosures are made with provisions for it.

The graphic below shows what would be the majority of installations in the South East.


1100203955_2.jpg


Roger
 
iwire said:
I don't think so.

Bonding is many things as the definition shows, it is not limited to connecting raceway to a meter socket with a conductor.

When you put conductor from a receptacle to a box you are bonding.

When you attach a GEC to a grounded conductor you are bonding.



Yeah your right we should ignore the NEC definition as a matter of fact Article 100 should be removed all together as it only serves to confuse.
icon12.gif

I didn't say ignore.
You need to understand what purpose the definitions serve. . If you don't then you'll read the definition of "grounded" and come to the conclusion that the electrode grounding conductor is the grounded conductor. . Then everywhere you go in the code to find requirements of the grounded conductor you'll end up confused.

The definitions define words they don't define function.
The electrode grounding conductor does not function as the grounded conductor.

"should be removed all together as it only serves to confuse"
No, should be understood for what they are or they will only serve to confuse.

David
 
dnem said:
I didn't say ignore.
You need to understand what purpose the definitions serve.

I do understand them.

It appears the definitions do not fit your idea of what they should mean.

Simply yes or no question.

When I attach the grounding electrode conductor to the grounded conductor am I bonding them?
 
iwire said:
Simply yes or no question.

When I attach the grounding electrode conductor to the grounded conductor am I bonding them?

Yes

iwire said:
I do understand them.

It appears the definitions do not fit your idea of what they should mean.

Simply multiple choice
Tell me which conductor serves the following function.

Connected to earth or to some conducting body that serves in place of earth. .

1) ungrounded
2) grounded
3) equipment grounding
4) electrode grounding

Now tell me which Article100 word that is a definition of.

1) ungrounded
2) grounded
3) equipment grounding
4) electrode grounding

David
 
roger said:
Stickboy, you're reading the wrong definition, we are not talking about Accessible, we are talking about Accessible (as applied to wiring methods)




Where do you see a lock in that definition?

Unless the meter enclosure is behind the building finish the wiring in it is accessible

Why do you think it's a code violation to make the connection in the meter can in the first place? I know you say your POCO doesn't allow it but that has nothing to do with the NEC.

It is a common practice and the meter enclosures are made with provisions for it.

The graphic below shows what would be the majority of installations in the South East.


1100203955_2.jpg


Roger
I agree 100%!!! I would love to bond the ground rods in the meter, it would save me alot of extra work but I would never get a service energized if I did.... what can I tell you? Connecticut is different, we can't buy beer after 8:00pm except in a bar either....
 
stickboy1375 said:
what can I tell you? Connecticut is different, we can't buy beer after 8:00pm except in a bar either....

sad-smiley-023.gif




What, all this other stuff you and I have been talking about doesn't seem important now.


BTW, If I haven't said it Welcome to the Forum.