LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Feb 11, 2022 #21 Tulsa Electrician said: 'No TA or locknuts, it is just a sleeve protecting the GEC, Click to expand... Gotcha.
Tulsa Electrician said: 'No TA or locknuts, it is just a sleeve protecting the GEC, Click to expand... Gotcha.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Feb 12, 2022 #22 petersonra said: I don't doubt that it is "better". I doubt it matters all that much one way or the other. Click to expand... A wire running thru a ferrous raceway,where the wire is not bonded to each end of the raceway, will restrict 97% of the current from lightning. My source is is the IEEE green book on grounding.
petersonra said: I don't doubt that it is "better". I doubt it matters all that much one way or the other. Click to expand... A wire running thru a ferrous raceway,where the wire is not bonded to each end of the raceway, will restrict 97% of the current from lightning. My source is is the IEEE green book on grounding.