The conductors that are EXPECTED / REQUIRED to be part of the GES have to be sized per 250.66
The conductors that are
not EXPECTED / REQUIRED to be part of the GES have to be sized per 250.122
Only if you choose to ignore the NEC requirements contained in 250.50
Again, the EGC between separate buildings does not perform the same function as the GEC inside a single building.
It is that simple.