Grounding Electrode For a Service on a Bridge

Status
Not open for further replies.

Sthome25

Member
Location
Coatesville, PA
Occupation
Electrician
I have an odd situation. I will be updating a service that is located in the center of a steel bridge. The service (60 Amp) is for street lights and eventually some cameras. The AHJ (PennDOT) typically requires (2) 8' ground rods, but that doesnt work in the middle of a bridge. I am thinking that I can put a lug to the steel framing of the bridge at the service and at the end of the bridge, then set the two rods on the side of the bridge where the service is fed from (pole mounted transfromer). Any other insight on this situation would be greatly appreciated.

PA is currently using the 2014 NEC.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

I would counter that you have a great Ufer grounding electrode, and you should only need to bond to the bridge itself.
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Sounds reasonable. Refer to 250.68(B) & (C)(2). Seems as though a GES would have been on the engineered drawings.
 

Sthome25

Member
Location
Coatesville, PA
Occupation
Electrician
Sounds reasonable. Refer to 250.68(B) & (C)(2). Seems as though a GES would have been on the engineered drawings

250.68(C)(2) should satisfy my PennDOT inspector. Thank you for the reference, I overlooked that paragraph. The engineered drawings I get are not that good. I get a line showing an electrode and note indicating 2 ground rods. Thanks for the help!
 

102 Inspector

Senior Member
Location
N/E Indiana
Occupation
Inspector- All facets
Would they have to be 8 foot anchors and how do you guarantee they are in direct contact? I agree, the UFER is already provided and bonding only additional.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
250.68(C)(2) should satisfy my PennDOT inspector. Thank you for the reference, I overlooked that paragraph. The engineered drawings I get are not that good. I get a line showing an electrode and note indicating 2 ground rods. Thanks for the help!
That’s because the engineer was lazy! LOL!
 