Good Morning Guys,
I have a project where we are setting a service on the utility company trough. This trough is fed from a bolted pressure switch where the neutral and ground are bonded. The utility company does not allow a ground in there trough so we will have to tap on to the building steel to get aduquate grounding or split bolt to the grounding electrode coming out of the bolted pressure switch. my question is, is should this be sized per 250.122 pr 250.66 and where is this senario mentioned in article 250. my optinion is that it is a EG conductor.
Thanks,
I have a project where we are setting a service on the utility company trough. This trough is fed from a bolted pressure switch where the neutral and ground are bonded. The utility company does not allow a ground in there trough so we will have to tap on to the building steel to get aduquate grounding or split bolt to the grounding electrode coming out of the bolted pressure switch. my question is, is should this be sized per 250.122 pr 250.66 and where is this senario mentioned in article 250. my optinion is that it is a EG conductor.