Does each piece of equipment connected from a tap in the service end box get a connection to a grounding electrode with a grounding electrode conductor?
If the GEC is run to a point ahead of multiple disconnecting means - no, if GEC does not run to such a point, you need to hit every disconnecting means with a GEC. You can run a GEC to each disconnect or you can run a common GEC and make taps to each disconnect. The taps or individual runs to each disconnect only need sized per the conductors supplying the disconnect, the common GEC must be sized per the equivalent service (or feeder) conductors where there are multiple conductors per phase making up the supply.Thanks but each does require a connection to the grounding electrode?