Given an 800 amp service, with grounding avaialbe to building steel, metallic water pipie, and made electrodres (ground rods), Would the grounding conductor size to the building steel and water line be 1/0 copper in accordance with Table 250.66? Would the conductor size to the ground rods then be sized at #6 copper in accordance with 250.66 (A)? Had a contractor run 1/0 to ground rods and I thought the maximum required was #6 with protection, #4 if protection against physical damage was not provided. Any assistance or comments?