Re: GROUNDING ELECTRODE SYSTEM AND MAIN BONDING JUMPER
Originally posted by floyd:
... Primary service coming to the transformer is 12,470 volts and owned by the military installation. Secondary voltage is 120/208 volts, 3 phase. ...
floyd -
Who owns what? More importantly, where is the service point?
Even more important, Who is making the rules? Doesn't the Corps of Engineers have their own code that should be followed? This is kind of important cause it's their ball and their playing field. :roll: Note: May match the NEC most places, but does vary. For example, i understand the gound rod resistance is required to be 10 ohms - no give-me for an extra rod.
So, by the NEC/NESC, assuming the service point is ahead of the xfmr primary: A few of the sites I work are industrial installations where the service is HV from the utility. The HV disconnect is our's and that is the service. The transformer is ours.
That makes the transformer secondary a separately derived system. From there, the xfmr neutral can be grounded and bonded and five wires run to the 208 panel/switchboard - separate ground and neutral - and that meets NEC and I think is a good method.
If the transformer belonged to the utility, the practice, per the NESC, (note: not verified by me) is to ground and bond the neutral at the xfmr, four wires to the 208 panel/switchboard, with the neutral grounded and bonded again.
This also meets code (NESC and NEC). IMO this is not as good a method as the first. But it is the method used in every house in the US. (For the regimented, literal sorts, "Oddball exceptions noted."
So, what's not to like?
carl