Grounding electrodes and Equipment Grounding Conductors Parallel

Rell

Super
Location
California
Occupation
Apprentice
How do I size Grounding electrodes and Equipment Grounding Conductors for Parallel Feeders? Do I double the size listed in the table?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No, are you running the GEC within the same raceways as the feeder? The EGC is based on the OCPD upstream of the feeder and Table 250.122 and is the same size in each parallel raceway.
 