ins.GDF said:Should structural steel be bonded to GES if underground metal water pipe and ground rod electrodes are being used as grounding electrodes.![]()
Yes, and 'bonded' is the right word. If building steel ever became energized, you'd want the pathway to the system grounded conductor to have as low an impedance as possible. That's why the conductor size is based on service capability.ins.GDF said:Should structural steel be bonded to GES if underground metal water pipe and ground rod electrodes are being used as grounding electrodes.![]()
LarryFine said:If building steel ever became energized, you'd want the pathway to the system grounded conductor to have as low an impedance as possible. That's why the conductor size is based on service capability.
I understand, like you understand most of the things I say. :smile: I just like throwing stuff in that I think helps make a better mental image to those who almost get it. Knowing why we do what we do often helps when faced with an unexpected situation.iwire said:Larry do not forget that building steel is not just being bonded for that reason, it is in most case a grounding electrode.